- Help Center
- Automation/Electrical
- Programmable Relays
-
Pneumatics
- Air Cylinders
- Air Dryers
- Auto Switches
- Boosters
- Electric Actuators
- Fieldbus System/Serial Transmission System
- Fittings
- Modular F.R.L.
- Pressure Switches
- Regulators
- Rotary Actuators
- Solenoid Valve
- Temperature Control Equipment
- Vacuum Equipment
- Photoelectric Sensors
- Process Valves
- Valve Clamps and Accessories
- Pumps
- Additional Articles in Pneumatics
- Safety Valves
- Tubing
-
Hydraulics
-
Automation/Electrical
- Contact Sensors / Liquid Leakage Sensors
- Level Switches
- Basic Switches
- Limit Switches
- Push Buttons / Indicator Lamps
- Thumbwheel Switches
- Safety Limit Switches
- Temperature Controllers
- Counters
- Programmable Relays
- Programmable Controllers
- Safety Sensors
- Safety Door Switches
- Solid-state Relays
- Timers
- Inverters
- Power Supplies
- Axial Fans
- Wiring Systems
- Rotary Encoders
- Pressure Sensors
- Displacement Sensors/Measurement Sensors
- Ultrasonic Sensors
- Emergency Stop Switches
- Power Controllers
- Signal Converters
- Machine Automation Controllers
- RFID Systems
- Measuring / Motor Protective Relays
- Vision Sensors / Machine Vision Systems
- Photomicro Sensors
- Digital Panel Indicators
- Programmable Terminals
- Servomotors / Servo Drivers
- Proximity Sensors
- General Purpose Relays
- Fieldbus Communications
-
Safety
-
Website Help Center
ZEN Programmable Relays: Can I use AC 2-wire sensors?
AC 2-wire sensors cannot be connected directly to the AC input of the ZEN. To connect a 2-wire sensor, insert a relay between the sensor and the ZEN or connect external bleeder resistance.
Example: Connecting to a CPU Unit or Expansion I/O Unit
a) Use a resistance that satisfies both of the following conditions.
b) Because of heat generation, use a resistor with at least the following wattage.
Note:
Calculating the Bleeder Resistance when Connecting an OMRON E2E-X10Y 2-Wire AC Sensor
This calculations in this example are based on an input voltage of 85 to 110 V AC.
The following values are from the Sensor datasheet.
The Sensor's maximum leakage current is 1.7 mA.
The minimum current when the Sensor's OFF residual voltage is 25 V or less (i.e., the OFF voltage for the EN) is 5 mA, as shown in the residual voltage characteristic graph.
From the formulas given above,
R1 ≤ 25 V AC/1.7 mA = 14.7 kΩ
R2 ≤ 85 V AC/5 mA = 17 kΩ
The bleeder resistor must thus be 14 kΩ
The Sensor output current in this case would be 100 VAC/14 kΩ, or 7 mA. This satisfies the Sensor's control output range of 5 to 300 mA.
The bleeder resistor capacity is calculated as shown below and must be 3 W.
P ≥ (110 V AC2)/14 kΩ × 3 = 2.59 W