- Help Center
- Automation/Electrical
- Solid-state Relays
-
Pneumatics
- Air Cylinders
- Air Dryers
- Auto Switches
- Boosters
- Electric Actuators
- Fieldbus System/Serial Transmission System
- Fittings
- Modular F.R.L.
- Pressure Switches
- Regulators
- Rotary Actuators
- Solenoid Valve
- Temperature Control Equipment
- Vacuum Equipment
- Photoelectric Sensors
- Process Valves
- Valve Clamps and Accessories
- Pumps
- Additional Articles in Pneumatics
- Safety Valves
- Tubing
-
Hydraulics
-
Automation/Electrical
- Contact Sensors / Liquid Leakage Sensors
- Level Switches
- Basic Switches
- Limit Switches
- Push Buttons / Indicator Lamps
- Thumbwheel Switches
- Safety Limit Switches
- Temperature Controllers
- Counters
- Programmable Relays
- Programmable Controllers
- Safety Sensors
- Safety Door Switches
- Solid-state Relays
- Timers
- Inverters
- Power Supplies
- Axial Fans
- Wiring Systems
- Rotary Encoders
- Pressure Sensors
- Displacement Sensors/Measurement Sensors
- Ultrasonic Sensors
- Emergency Stop Switches
- Power Controllers
- Signal Converters
- Machine Automation Controllers
- RFID Systems
- Measuring / Motor Protective Relays
- Vision Sensors / Machine Vision Systems
- Photomicro Sensors
- Digital Panel Indicators
- Programmable Terminals
- Servomotors / Servo Drivers
- Proximity Sensors
- General Purpose Relays
- Fieldbus Communications
-
Safety
-
Website Help Center
What should be done about surge-absorbing circuits for AC-load Solid-state Relays?
Measures against AC Switching Solid-state Relay Output Noise Surges
1. The Solid-state Relay has a built-in snubber circuit to smooth out a sudden rise in voltage. If there is a large voltage surge in the output-side AC power supply, the snubber circuit will not be sufficient to suppress the surge, and overvoltage will damage the output elements.
2. The following models have a built-in surge-absorbing varistor:
G3NA, G3S, G3PA, G3PB, G3NE, G3J, G3NH, G9H, G3DZ (some models), G3RZ, G3FM
3. Be sure to take measures against surge when switching an inductive load with an Solid-state Relay that does not have a built-in surge-absorbing element. (Refer to the following figure.)
Note: A separate varistor with a surge resistance higher than the built-in varistor must be mounted externally if influence is possible from noise that is not completely absorbed by the built-in varistor (surge resistance: 700 to 1000 A).
Select a surge-absorbing element that meets the conditions in the following table.
Voltage | Varistor voltage | Surge resistance |
100 to 120VAC | 240 to 270 V | 1,000 A min. |
200 to 240VAC | 440 to 470 V | |
380 to 480VAC | 820 to 1,000 V |