- Help Center
- Automation/Electrical
- Pressure Sensors
-
Pneumatics
- Air Cylinders
- Air Dryers
- Auto Switches
- Boosters
- Electric Actuators
- Fieldbus System/Serial Transmission System
- Fittings
- Modular F.R.L.
- Pressure Switches
- Regulators
- Rotary Actuators
- Solenoid Valve
- Temperature Control Equipment
- Vacuum Equipment
- Photoelectric Sensors
- Process Valves
- Valve Clamps and Accessories
- Pumps
- Additional Articles in Pneumatics
- Safety Valves
- Tubing
-
Hydraulics
-
Automation/Electrical
- Contact Sensors / Liquid Leakage Sensors
- Level Switches
- Basic Switches
- Limit Switches
- Push Buttons / Indicator Lamps
- Thumbwheel Switches
- Safety Limit Switches
- Temperature Controllers
- Counters
- Programmable Relays
- Programmable Controllers
- Safety Sensors
- Safety Door Switches
- Solid-state Relays
- Timers
- Inverters
- Power Supplies
- Axial Fans
- Wiring Systems
- Rotary Encoders
- Pressure Sensors
- Displacement Sensors/Measurement Sensors
- Ultrasonic Sensors
- Emergency Stop Switches
- Power Controllers
- Signal Converters
- Machine Automation Controllers
- RFID Systems
- Measuring / Motor Protective Relays
- Vision Sensors / Machine Vision Systems
- Photomicro Sensors
- Digital Panel Indicators
- Programmable Terminals
- Servomotors / Servo Drivers
- Proximity Sensors
- General Purpose Relays
- Fieldbus Communications
-
Safety
-
Website Help Center
What is the procedure for setting the pressure of E8F2 Pressure Sensor manually?
Manual Setting
Note: Manual setting can be performed if is selected for the pressure setting method in the initial settings.
1. Press to enter the pressure setting mode, and and the set ON point for OUT1 will be alternately displayed.
2. Change the ON point (for OUT1) using and .
3. Press to select the displayed ON point, and and the set OFF point for OUT1 will be alternately displayed.
4. Change the OFF point (for OUT1) using and .
5. Press to select the displayed OFF point, and and the set ON point for OUT2 will be alternately displayed.
6. Change the ON point (for OUT2) using and .
7. Press to select the displayed ON point, and and the set OFF point for OUT2 will be alternately displayed.
8. Change the OFF point (for OUT2) using and .
9. Press to select the displayed OFF point, and and the set ON point for OUT1 will be alternately displayed.
Returning to Measurement Mode
Saving the set value: Press for approx. 2 s. (Valid for any set value display.)
Not saving the set value: Press and at the same time. (Valid for any set value display.)