- Help Center
- Automation/Electrical
- Displacement Sensors/Measurement Sensors
-
Pneumatics
- Air Cylinders
- Air Dryers
- Auto Switches
- Boosters
- Electric Actuators
- Fieldbus System/Serial Transmission System
- Fittings
- Modular F.R.L.
- Pressure Switches
- Regulators
- Rotary Actuators
- Solenoid Valve
- Temperature Control Equipment
- Vacuum Equipment
- Photoelectric Sensors
- Process Valves
- Valve Clamps and Accessories
- Pumps
- Additional Articles in Pneumatics
- Safety Valves
- Tubing
-
Hydraulics
-
Automation/Electrical
- Contact Sensors / Liquid Leakage Sensors
- Level Switches
- Basic Switches
- Limit Switches
- Push Buttons / Indicator Lamps
- Thumbwheel Switches
- Safety Limit Switches
- Temperature Controllers
- Counters
- Programmable Relays
- Programmable Controllers
- Safety Sensors
- Safety Door Switches
- Solid-state Relays
- Timers
- Inverters
- Power Supplies
- Axial Fans
- Wiring Systems
- Rotary Encoders
- Pressure Sensors
- Displacement Sensors/Measurement Sensors
- Ultrasonic Sensors
- Emergency Stop Switches
- Power Controllers
- Signal Converters
- Machine Automation Controllers
- RFID Systems
- Measuring / Motor Protective Relays
- Vision Sensors / Machine Vision Systems
- Photomicro Sensors
- Digital Panel Indicators
- Programmable Terminals
- Servomotors / Servo Drivers
- Proximity Sensors
- General Purpose Relays
- Fieldbus Communications
-
Safety
-
Website Help Center
The threshold value cannot be set. What is causing this, and what can be done to resolve it?
Cause 1:
The HIGH threshold value is set lower than the LOW threshold value.
In this case, the following error message will be displayed.
Display | Cause |
(flashing) |
Attempted to set the LOW threshold value higher than the HIGH threshold value |
(flashing) |
Attempted to set the HIGH threshold value lower than the LOW threshold value |
Remedy 1:
Make sure that the HIGH threshold value is set higher than the LOW threshold value.
Cause 2:
The hysteresis (Hys) is too high. If this is the case, the difference between the HIGH threshold value and the LOW threshold value is smaller than the hysteresis value, so that a PASS judgment is not possible. The setting is thus not allowed.
Remedy 2:
Make the hysteresis value smaller to avoid the condition described above.