- Help Center
- Automation/Electrical
- Programmable Controllers
-
Pneumatics
- Air Cylinders
- Air Dryers
- Auto Switches
- Boosters
- Electric Actuators
- Fieldbus System/Serial Transmission System
- Fittings
- Modular F.R.L.
- Pressure Switches
- Regulators
- Rotary Actuators
- Solenoid Valve
- Temperature Control Equipment
- Vacuum Equipment
- Photoelectric Sensors
- Process Valves
- Valve Clamps and Accessories
- Pumps
- Additional Articles in Pneumatics
- Safety Valves
- Tubing
-
Hydraulics
-
Automation/Electrical
- Contact Sensors / Liquid Leakage Sensors
- Level Switches
- Basic Switches
- Limit Switches
- Push Buttons / Indicator Lamps
- Thumbwheel Switches
- Safety Limit Switches
- Temperature Controllers
- Counters
- Programmable Relays
- Programmable Controllers
- Safety Sensors
- Safety Door Switches
- Solid-state Relays
- Timers
- Inverters
- Power Supplies
- Axial Fans
- Wiring Systems
- Rotary Encoders
- Pressure Sensors
- Displacement Sensors/Measurement Sensors
- Ultrasonic Sensors
- Emergency Stop Switches
- Power Controllers
- Signal Converters
- Machine Automation Controllers
- RFID Systems
- Measuring / Motor Protective Relays
- Vision Sensors / Machine Vision Systems
- Photomicro Sensors
- Digital Panel Indicators
- Programmable Terminals
- Servomotors / Servo Drivers
- Proximity Sensors
- General Purpose Relays
- Fieldbus Communications
-
Safety
-
Website Help Center
How will Programmable Controllers behave if the power supply voltage drops momentarily?
The Programmable Controllers behaves in the following ways if the power supply is interrupted or the power supply voltage drops.
If the power supply falls below 85% of the rated voltage, the CPU Unit will detect a momentary power interruption, will stop operation, and will turn OFF the outputs depending on the length of the interruption.
The CPU Unit will not respond to the power interruption and will continue to run unconditionally if the power is interrupted for less than 10 ms
If the power interruption lasts more than 10 ms but less than 25 ms, the CPU Unit may or may not respond to the power interruption. In this case, the operation of the CPU Unit cannot be predicted.
The CPU Unit will stop unconditionally if the power interruption lasts more than 25 ms.