- Help Center
- Automation/Electrical
- General Purpose Relays
-
Pneumatics
- Air Cylinders
- Air Dryers
- Auto Switches
- Boosters
- Electric Actuators
- Fieldbus System/Serial Transmission System
- Fittings
- Modular F.R.L.
- Pressure Switches
- Regulators
- Rotary Actuators
- Solenoid Valve
- Temperature Control Equipment
- Vacuum Equipment
- Photoelectric Sensors
- Process Valves
- Valve Clamps and Accessories
- Pumps
- Additional Articles in Pneumatics
- Safety Valves
- Tubing
-
Hydraulics
-
Automation/Electrical
- Contact Sensors / Liquid Leakage Sensors
- Level Switches
- Basic Switches
- Limit Switches
- Push Buttons / Indicator Lamps
- Thumbwheel Switches
- Safety Limit Switches
- Temperature Controllers
- Counters
- Programmable Relays
- Programmable Controllers
- Safety Sensors
- Safety Door Switches
- Solid-state Relays
- Timers
- Inverters
- Power Supplies
- Axial Fans
- Wiring Systems
- Rotary Encoders
- Pressure Sensors
- Displacement Sensors/Measurement Sensors
- Ultrasonic Sensors
- Emergency Stop Switches
- Power Controllers
- Signal Converters
- Machine Automation Controllers
- RFID Systems
- Measuring / Motor Protective Relays
- Vision Sensors / Machine Vision Systems
- Photomicro Sensors
- Digital Panel Indicators
- Programmable Terminals
- Servomotors / Servo Drivers
- Proximity Sensors
- General Purpose Relays
- Fieldbus Communications
-
Safety
-
Website Help Center
How do you use the durability curve?
The durability curve is used to check the maximum switching capacity (expected service life).
The following example will be used to describe how to find the maximum switching capacity of a contact at a particular contact current.
Look at the graph to determine what is the expected service life of Relays with 1-A contact current and 20-VDC resistive load.
MY4 General-purpose Relays
1. Draw a vertical line where the switching current is 1 A (red line).
2. Draw a horizontal line from the point of intersection with the 30-VDC resistive load curve (green line).
3. Where the green line intersects with the durability axis is the expected service life. In this case, the expected number of operations is 700,000 operations.
Example:
What is the expected service life for a 220-VAC 2-A resistive load?
Answer:
Approximately 400,000 operations (blue line).