- Help Center
- Automation/Electrical
- General Purpose Relays
-
Pneumatics
- Air Cylinders
- Air Dryers
- Auto Switches
- Boosters
- Electric Actuators
- Fieldbus System/Serial Transmission System
- Fittings
- Modular F.R.L.
- Pressure Switches
- Regulators
- Rotary Actuators
- Solenoid Valve
- Temperature Control Equipment
- Vacuum Equipment
- Photoelectric Sensors
- Process Valves
- Valve Clamps and Accessories
- Pumps
- Additional Articles in Pneumatics
- Safety Valves
- Tubing
-
Hydraulics
-
Automation/Electrical
- Contact Sensors / Liquid Leakage Sensors
- Level Switches
- Basic Switches
- Limit Switches
- Push Buttons / Indicator Lamps
- Thumbwheel Switches
- Safety Limit Switches
- Temperature Controllers
- Counters
- Programmable Relays
- Programmable Controllers
- Safety Sensors
- Safety Door Switches
- Solid-state Relays
- Timers
- Inverters
- Power Supplies
- Axial Fans
- Wiring Systems
- Rotary Encoders
- Pressure Sensors
- Displacement Sensors/Measurement Sensors
- Ultrasonic Sensors
- Emergency Stop Switches
- Power Controllers
- Signal Converters
- Machine Automation Controllers
- RFID Systems
- Measuring / Motor Protective Relays
- Vision Sensors / Machine Vision Systems
- Photomicro Sensors
- Digital Panel Indicators
- Programmable Terminals
- Servomotors / Servo Drivers
- Proximity Sensors
- General Purpose Relays
- Fieldbus Communications
-
Safety
-
Website Help Center
How do you find the maximum switching capacity?
This following graph can be used to find how much current can be applied to the contacts. A description of how to interpret the graph to find out how much current can be applied at what load circuit voltage (contact voltage) is provided below.
The following figure shows how to find the maximum switching capacity for a 200-VAC inductive load.
1. Draw a vertical line where the contact voltage is 200 V (red line).
2. Draw a horizontal line from the point of intersection with the AC inductive load curve (green line).
3. Where the green line intersects the contact current axis is the maximum switching capacity. In this case, the switching capacity is 0.9 A.
Example:
To what voltage must the contact voltage be limited in order to switch a 0.5-A DC inductive load?
Answer:
Keep the voltage below 50 VDC (blue line).