- Help Center
- Automation/Electrical
- Measuring / Motor Protective Relays
-
Pneumatics
- Air Cylinders
- Air Dryers
- Auto Switches
- Boosters
- Electric Actuators
- Fieldbus System/Serial Transmission System
- Fittings
- Modular F.R.L.
- Pressure Switches
- Regulators
- Rotary Actuators
- Solenoid Valve
- Temperature Control Equipment
- Vacuum Equipment
- Photoelectric Sensors
- Process Valves
- Valve Clamps and Accessories
- Pumps
- Additional Articles in Pneumatics
- Safety Valves
- Tubing
-
Hydraulics
-
Automation/Electrical
- Contact Sensors / Liquid Leakage Sensors
- Level Switches
- Basic Switches
- Limit Switches
- Push Buttons / Indicator Lamps
- Thumbwheel Switches
- Safety Limit Switches
- Temperature Controllers
- Counters
- Programmable Relays
- Programmable Controllers
- Safety Sensors
- Safety Door Switches
- Solid-state Relays
- Timers
- Inverters
- Power Supplies
- Axial Fans
- Wiring Systems
- Rotary Encoders
- Pressure Sensors
- Displacement Sensors/Measurement Sensors
- Ultrasonic Sensors
- Emergency Stop Switches
- Power Controllers
- Signal Converters
- Machine Automation Controllers
- RFID Systems
- Measuring / Motor Protective Relays
- Vision Sensors / Machine Vision Systems
- Photomicro Sensors
- Digital Panel Indicators
- Programmable Terminals
- Servomotors / Servo Drivers
- Proximity Sensors
- General Purpose Relays
- Fieldbus Communications
-
Safety
-
Website Help Center
Can SE Motor Protective Relays be used for motors with a rated current of 1 A or less?
Yes, you can do this by using the SET-3A Current Converters. Set the primary conductor runs to 20 passes, and set the tap setting to 20.
*The current scale multiplying factor will be 0.1.
Example: Using the SET-3A and a Tap Setting of 20
Reference
Rated current (stable current range) (A) |
Current Converter | ||
Passes | Tap setting | Model | |
0.4 to 1 | 20 | 20 | SET-3A |
0.8 to 2 | 10 | 20 | |
4 to 10 | 2 | 20 | |
8 to 20 | 1 | 20 |
Note: (Tap setting)/ (Passes) = Maximum scale (10) value
Interpreting the Above Table:
In the darkly shaded row, the rated current range can be set to 0.4 to 1 A with 20 passes. This can be used for motors of 1 A or less. Refer to the following explanations to determine the number of primary conductor runs (passes) and the tap setting.
Determining the Number of Primary Conductor Passes
Pass all three wires through the holes from the same direction. It doesn't matter which wires go through which holes.