- Help Center
- Automation/Electrical
- Solid-state Relays
-
Pneumatics
- Air Cylinders
- Air Dryers
- Auto Switches
- Boosters
- Electric Actuators
- Fieldbus System/Serial Transmission System
- Fittings
- Modular F.R.L.
- Pressure Switches
- Regulators
- Rotary Actuators
- Solenoid Valve
- Temperature Control Equipment
- Vacuum Equipment
- Photoelectric Sensors
- Process Valves
- Valve Clamps and Accessories
- Pumps
- Additional Articles in Pneumatics
- Safety Valves
- Tubing
-
Hydraulics
-
Automation/Electrical
- Contact Sensors / Liquid Leakage Sensors
- Level Switches
- Basic Switches
- Limit Switches
- Push Buttons / Indicator Lamps
- Thumbwheel Switches
- Safety Limit Switches
- Temperature Controllers
- Counters
- Programmable Relays
- Programmable Controllers
- Safety Sensors
- Safety Door Switches
- Solid-state Relays
- Timers
- Inverters
- Power Supplies
- Axial Fans
- Wiring Systems
- Rotary Encoders
- Pressure Sensors
- Displacement Sensors/Measurement Sensors
- Ultrasonic Sensors
- Emergency Stop Switches
- Power Controllers
- Signal Converters
- Machine Automation Controllers
- RFID Systems
- Measuring / Motor Protective Relays
- Vision Sensors / Machine Vision Systems
- Photomicro Sensors
- Digital Panel Indicators
- Programmable Terminals
- Servomotors / Servo Drivers
- Proximity Sensors
- General Purpose Relays
- Fieldbus Communications
-
Safety
-
Website Help Center
Are Solid-state Relays unable to switch microloads?
The minimum load currents in the following table can be switched using Solid-state Relays with Power MOS FET outputs (G3DZ/G3RZ).
Minimum Load Currents for G3DZ and G3RZ
Load voltage | G3DZ | G3RZ |
200 VAC | 100 μA | 100 μA |
100 VAC | 10 μA | 100 μA |
The following applies to AC Solid-state Relays with triac or thyristor outputs and to DC Solid-state Relays with power transistor outputs.
Solid-state Relays with AC Output:
At present, the minimum load current for most Solid-state Relays is 100 mA (50 mA at an ambient temperature of 25°C or higher) considering the degree of current (holding current) required because of problems with the load failing to reset due to leakage current and the output elements remaining ON.
Microloads below these values can be supported by connecting bleeder resistance in parallel with the load. By using MOS FETs, however, microloads can be directly switched without bleeder resistance.
100 VAC | 5 to 10 kΩ | 3 W |
200 VAC | 5 to 10 kΩ | 15 W |
Solid-state Relays with DC Output:
Leakage current may cause the load to fail to reset.
There is generally no problem for most microload switching with Solid-state Relay models with a leakage current of 0.1 mA or less. Caution is required, however, for G3CN-D Solid-state Relays, G3FD Solid-state Relays, G3HD Solid-state Relaysand other models with large leakage current.
The following table provides a rough guide to bleeder resistance if reset failure occurs using the G3CN-D, G3FD, or G3HD.
5 VDC | 1.6 kΩ | 1/4 W |
12 VDC | 620 Ω | 1 W |
24 VDC | 330 Ω | 5 W |